In our Data Center, we have a completely independant “A side” and “B side” power source. For equipment that has a Single Power Supply or (3) Power Supplies, we have implemented APC Transfer Switches that connect to both the A & B side feeds so we can maintain and N+1 redundancy. Through recent testing, we proved that you can shut off the A or B side and the opposite will support the entire Data Centers power load.
Given this design, our Facilities department would like to work on new power connections and/or Annual Preventative Maintenance to floor PDU’s (Power Distribution Units) Cold. Meaning that they could turn off the “A PDU” and connect up new items or complete Annual PM’s while the “B PDU” is still providing power to the room. They state that this would make the job Safer and that it would prevent any potential problems while hooking up 225a cables.
While I completely agree with them, there are a couple of folks in our organization that don’t. They would like the work to be done “hot”. Their feeling is that we would intentionally be removing the N+1 redundancy during that timeframe and wouldn’t have anything to fail over to if needed.
I would like to hear from others on how they handle this type of work in their Data Centers. I would also like to see a count for the frequency of these type of scheduled outages per year.